PSQL0001: Unable to create a PostgreSQL instance
Symptom
Instance creation fails with the following error messages:
Invalid PostgreSQL User Name and Password.
OR
Connection to PostgreSQL server failed.
Cause 1
PostgresBrowseAgent.log shows the following error during instance creation:
7991 21550700 08/21 12:50:34 ### libpqInterface :: ConnectDb() - Connection Info string: port = '5432' dbname = 'postgres' user = 'pg_backup_agent' connect_timeout = '' password = **********
7991 21550700 08/21 12:50:34 ### libpqInterface :: ValidateConnection() - eRRoR -- PQreset failed to reset the connection. Error:FATAL: no
pg_hba.conf entry for host "[local]", user "pg_backup_agent", database "postgres", SSL off
FATAL: no pg_hba.conf entry for host "[local]", user "pg_backup_agent", database "postgres", SSL off
Here "[local]" relates to a UNIX socket connection, and thus the pg_hba.conf file lacks an entry to enable the socket connection from cvd that spawns psql -u postgres [username] from working. This can be tested from the client as root.
Resolution 1
Ensure pg_hba.conf file has an applicable line to match the user. The default line below will allow all users to connect to the client via the UNIX socket, as part of a default PostgreSQL install. It may be hashed out.
local all all md5
Alternatively, you can use the variation below to make it secure:
local all $[username_entered_in_gui_for_instance_creation] md5
This will allow the user to connect to all databases locally via the UNIX socket.
Cause 2
PostgresBrowseAgent.log shows the following error during instance creation:
18041 1184f700 09/28 18:57:36 ### libpqInterface :: libpqInterface() - eRRoR -- Exception in [libpqInterface :: libpqInterface]
Type:[APPLICATION_EXCEPTION] Msg:[Lib dir is not present]
18041 1184f700 09/28 18:57:36 ### ExecutePostgre::init() - eRRoR --
Exception in [libpqInterface :: libpqInterface]
Type:[APPLICATION_EXCEPTION] Msg:[Lib dir is not present]
18041 1184f700 09/28 18:57:36 ### PostgresBrowseAgent::verifyUserInfo() -
connection failed
18041 1184f700 09/28 18:57:36 ### PostgresBrowseAgent::verifyUserInfo() -
exepg.postgre_exe failed
Resolution 2
Ensure the correct PostgreSQL lib directory is entered in the instance creation dialog. It must contain libpq.so library file (and other related library files). It is used to connect to the database and execute queries.
-
To locate the lib directory, run the following command:
bash-3.2# ./pg_config --libdirExample output:
/PostgreSQL/9.2/libIf pg_config is not present which is installed as part of PostgreSQL install, run the following command (on UNIX clients):
bash-3.2# locate libpq.soExample output:
/PostgreSQL/9.2/lib/libpq.so -
If the lib path contains libpq.so.x.x instead of libpq.so, create a symlink libpq.so to libpq.so.x.x before attempting instance creation.
For example:
On some setups libpq.so may not be present, but there will be a numbered version like libpq.so.4 or libpq.so.5.
In this case, create a symlink version of libpq.so pointing to the numbered one:
bash-3.2# ln -s $[/usr/lib64/libpq.so.x.x] $[/usr/lib64/libpq.so]You should be able to create instance successfully now.
Note
Library directory might differ for different setups. Find the proper library directory to create a soft link.
Cause 3
PostgresBrowseAgent.log shows the following error during instance creation:
24576 1026b700 09/28 23:10:39 ### PostgresBrowseAgent::verifyUserInfo() -
m_PostgresServer->GetConfigFilePath() = Commvault
24576 1026b700 09/28 23:10:39 ### libpqInterface :: ConnectDb() -
Connection Info string: port = '5432' dbname = 'commvault' user = 'commvault'
connection_timeout = '' password = **********
24576 1026b700 09/28 23:10:39 ### libpqInterface :: IsSuperUser() - eRRoR
- Exception in [libpqInterface :: IsSuperUser]
Type:[APPLCATION_EXCEPTION] Msg:[The user is not a super user]
24576 1026b700 09/28 23:10:39 ### libpqInterface :: libpqInterface() -
eRRoR - Exception in [libpqInterface :: IsSuperUser]
Type:[APPLCATION_EXCEPTION] Msg:[The user is not a super user]
24576 1026b700 09/28 23:10:39 ###ExecutePostgre::init() - eRRoR -
Exception in [libpqInterface :: IsSuperUser] ]
Type:[APPLCATION_EXCEPTION] Msg:[The user is not a super user]
24576 1026b700 09/28 23:10:39 ### PostgresBrowseeAgent::verifyUseerInfo()
- connection failed
24576 1026b700 09/28 23:10:39 ###PostgresBrowseeAgent::verifyUseerInfo()
- exepg.postgre.exe failed
24576 1026b700 09/28 23:10:39 ### PostgresBrowseeAgent::BrowseDBs() -
verifyUser failed (err=)
24576 1026b700 09/28 23:10:39 ### PostgresBrowseeAgent::DoBrowse() -
BrowseDBs failed. M_errorNum = 1577058305
24576 1026b700 09/28 23:10:39 ###
PostgresBrowseeAgent::SendBrowseResponse() - Sending mstype =
POSTGRESQL_BROWSE_FAILED
24576 1026b700 09/28 23:10:39 ### Main() - DoBrowse() failed
Here, the user provided in the instance creation dialog box doesn't have the necessary usesuper or superuser attribute.
Resolution 3
Use the following steps to add the superuser attribute to the user:
-
Once connected to PostgreSQL, run the following query to check if the usesuper attribute is incorrectly set:
select * from pg_user;
In the screenshot above, the commvault user has a f set against usesuper attribute. Instance creation using this user will therefore generate the above error.
-
When connected to PostgreSQL as superuser, run the following query to add the attribute:
PGSQL> ALTER USER username WITH superuser; -
Run the following query again to check if the attribute now shows a t against usesuper attribute.
select * from pg_user;
Cause 4
PostgresBrowseAgent.log shows the following error during instance creation due to the PostgreSQL server connection failure.
25925 ae3d6740 03/06 16:35:25 ### libpqInterface :: ConnectDb() - Connection Info string: port = '5433' dbname = 'postgres' user = 'postgres' connect_timeout = ' password = **********
25925 ae3d6740 03/06 16:35:25 ### libpqInterface :: ValidateConnection() - eRRoR -- PQreset failed to reset the connection. Error:FATAL: Peer authentication failed for user "postgres"
FATAL: Peer authentication failed for user "postgres"
25925 ae3d6740 03/06 16:35:25 ### libpqInterface :: ValidateConnection() - eRRoR -- Exception in [libpqInterface :: ValidateConnection] Type:[POSTGRE_EXCEPTION] Msg:[PQreset failed to reset the connection]
25925 ae3d6740 03/06 16:35:25 ### libpqInterface :: libpqInterface() - eRRoR -- Exception in [libpqInterface :: ValidateConnection] Type:[POSTGRE_EXCEPTION] Msg:[PQreset failed to reset the connection]
25925 ae3d6740 03/06 16:35:25 ### ExecutePostgre::init() - eRRoR -- Exception in [libpqInterface :: ValidateConnection] Type:[POSTGRE_EXCEPTION] Msg:[PQreset failed to reset the connection]
25925 ae3d6740 03/06 16:35:25 ### PostgresBrowseAgent::verifyUserInfo() - connection failed
25925 ae3d6740 03/06 16:35:25 ### PostgresBrowseAgent::verifyUserInfo() - exepg.postgre_exe failed
25925 ae3d6740 03/06 16:35:25 ### PostgresBrowseAgent::BrowseDBs() - verifyUser failed (err=)
Resolution 4
During instance creation, the software tries to connect to the PostgreSQL server as a root user. So, for successful peer authentication, add the following mappings in the pg_hba.conf and the pg_ident.conf files.
PostgreSQL application uses the first record with a matching connection type, client address, requested database, and user name to perform authentication. So, this entry should be added before other entries, if any other record matches the same conditions.
-
In the pg_hba.conf file, add the corresponding map name configured for the Postgres DB user as shown in the example below.
# TYPE DATABASE USER ADDRESS METHOD # "local" is for Unix domain socket connections only local all postgres peer map=testmap -
In the pg_ident.conf file, add mapping between the PostGres DB user and the system user 'root' as shown in the example below.
# Put your actual configuration here # ---------------------------------- # MAPNAME SYSTEM-USERNAME PG-USERNAME testmap postgres postgres testmap root postgres -
Now reload the PostgreSQL server using the following command:
select pg_reload_conf(); -
Before you retry creating an instance, verify the connection to the PostgreSQL database server.
Cause 5
PostgresBrowseAgent.log shows the following error during instance creation on an AIX client:
8519792 1 02/25 14:58:06 ### libpqInterface :: LoadlibpqSymbols() - dlopen failed:Could not load module /opt/freeware/lib64/libpq.so. Dependent module /usr/lib/libcrypto.a(libcrypto.so.1.0.1) could not be loaded.
PostgreSQL libpq.so library fails to load due to dependency issues.
Resolution 5
-
Copy the CvReIndexOpenSSL.sh script to the AIX client.
-
From the AIX client, navigate to the location where you have copied the CvReIndexOpenSSL.sh script, and run the following command:
CvReIndexOpenSSL.sh $[PGSQL-INSTALLATION-DIR>] $[COMMVAULT-BASE-DIR]For example,
./CvReIndexOpenSSL.sh $[/opt/freeware] $[/opt/CommVault/Base]Parameter
Description of Parameter Values
PGSQL-INSTALLATION-DIR
PostgreSQL installation directory
COMMVAULT-BASE-DIR
CommVault Base directory
-
Restart Commvault services in the client.
PSQL0004: PostgreSQL backup operation fails due to incorrect Archive Log directory configuration
Symptom
Backup operation fails with the following error messages:
Error Code: [94:13]
Description: PostgreSQL Database: [~WAL Archiving is NOT ENABLED. Please enable WAL Archiving for PostGres server.~] Data Backup Failed.
Source: kmlinsnap, Process: PostGresBackupParent
2388 b24 02/14 21:30:07 279 PGLogBackup :: GenerateCollectFile() - eRRoR -- Exception in [PGLogBackup :: GenerateCollectFile] Type:[POSTGRE_EXCEPTION] Msg:[Some log files are missing from the WAL dir]
2388 b24 02/14 21:30:07 279 PostGreLogBackupInterface() - eRRoR -- Exception in [PGLogBackup :: GenerateCollectFile] Type:[POSTGRE_EXCEPTION] Msg:[Some log files are missing from the WAL dir]
2388 b24 02/14 21:30:07 279 PostGresClBackupBase::Initialize() - Error generating collect file
Cause
The backup operation fails with the following errors in the PostGresBackupChild.log file:
6178 aed88300 01/24 11:01:21 247081 PostGreFsBackupInterface() - Enter
6178 aed88300 01/24 11:01:21 247081 libpqInterface :: ConnectDb() - Connection Info string: port = '5492' dbname = 'postgres' user = 'postgres' connect_timeout = '' password = **********
6178 aed88300 01/24 11:01:21 247081 PGFsBackup :: IsWALArchivingEnabled() - eRRoR -- Exception in [PGFsBackup :: IsWALArchivingEnabled] Type:[POSTGRE_EXCEPTION] Msg:[WAL archiving is not enabled]
6178 aed88300 01/24 11:01:21 247081 PGFsBackup :: PGFsBackup() - eRRoR -- Exception in [PGFsBackup :: IsWALArchivingEnabled] Type:[POSTGRE_EXCEPTION] Msg:[WAL archiving is not enabled]
6178 aed88300 01/24 11:01:21 247081 PostGreFsBackupInterface() - eRRoR -- Exception in [PGFsBackup :: IsWALArchivingEnabled] Type:[POSTGRE_EXCEPTION] Msg:[WAL archiving is not enabled]
6178 aed88300 01/24 11:01:21 247081 PostGresClBackupBase::Initialize() - Error generating collect file
2072 9b8 12/10 10:10:29 21565 libpqInterface :: AnalyzeResult() - eRRoR -- PQresultStatus indicates failure for SHOW archive_mode. Error:ERROR: unrecognized configuration parameter "archive_mode"
2072 9b8 12/10 10:10:29 21565 PGFsBackup :: IsWALArchivingEnabled() - Could not obtain the archive_mode setting.
2072 9b8 12/10 10:10:29 21565 PGFsBackup :: IsWALArchivingEnabled() - eRRoR -- Either provide a WAL archive command or enable EmptyWalArchiveCommand
Resolution
-
Check the permission for WAL directory. Postgres user and group should have read and write permissions to the WAL directory.
drwx------- 15 postgres postgres 4096 Jan 28 12:20 data drwxrwxrwx 2 postgres postgres 4096 Jan 28 12:20 wal -
Check whether the Archive Log Directory configured in the PostgreSQL instance properties and the postgresql.conf file is the same.
-
Follow all the checkpoints listed under Configuring the Archive Log Directory.
PSQL0005: FS based backup operation hangs due to incorrect permissions on the archive directory or incorrect archive command
Cause
FS backup copy operation can hang because the pg_stop_backup process hangs in the following cases:
-
There is an incorrect archive command specified in the 'postgresql.conf' file
-
There are incorrect permissions on the archive directory
-
There is insufficient free space in the volume or drive where archive log directory is present.
Resolution
Incorrect Archive Command
-
Run the following query to identify the hung pg_stop_backup process.
select datname,pid,usename,state,query from pg_stat_activity;For example,
postgres=# select datname,pid,usename,state,query from pg_stat_activity; datname | pid | usename | state | query postgres | 4903 | postgres | active | select pg_stop_backup(); postgres | 5089 | postgres | active | select datname,pid,usename,waitFor PostgreSQL version 9.5 or earlier, use the following query:
select datname,pid,usename,waiting,state,query from pg_stat_activity; -
Run the following query to terminate the hung pg_stop_backup process.
select pg_cancel_backend($[PID]);For example,
postgres=# select pg_cancel_backend($[4903]); pg_cancel_backend ------------------- t (1 row)For PostgreSQL version 9.5 or earlier, use the following query:
select pg_cancel_backend($[procpid]); -
Correct the archive command in the postgresql.conf file.
Example of a correct archive command
archive_command = '$[cp %p /vkm/PostgreSQL/9.3/wl/%f]' -
Restart the PostgreSQL server.
-
Verify that the archive command provided in the postgresql.conf file is correct. You can test this by running the following commands and verifying that they successfully complete.
For PostgreSQL version 15 and more recent versions:
select pg_backup_start('t', 'f'); select pg_backup_stop();For PostgreSQL versions 9.5 through 15:
select pg_start_backup(‘test’, 'f', 'f'); select pg_stop_backup('f');For PostgreSQL versions older than 9.5:
Select pg_start_backup(‘Testing’); Select pg_stop_backup(); -
Run a full PostgreSQL FS based backup operation.
Incorrect Permission on the archive directory
Verify that the PostgreSQL server user has the read, and write permissions on the archive directory.
PSQL0008: PostgreSQL dump based backup operation may fail with failure connecting to socket file
Symptom
Instance creation fails with the following error message:
Connection to PostgreSQL Server failed. Please check that PostgreSQL Server is Online, and has enough resources for normal operation. Check logs for more details.
Backup operation fails with the following error message:
Error Code: [94:15]
Description: PostgreSQL Database: [~template1~] Data Backup Failed with PostgreSQL Error: [~pg_dump: [archiver (db)] connection to database "template1" failed: could not connect to server: No such file or directory Is the server running locally and accepting connections on Unix domain socket "/var/run/postgresql/.s.PGSQL.5432"? ~].
Cause
The instance creation or the backup operation might fail because UNIX socket directory is not /tmp.
You will find the following errors in the PostGresBrowseAgent.log file for backup:
2719 a9f 10/17 15:54:56 ### ValidateConnection() - eRRoR -- PQreset failed to reset the connection. Error:could not connect to server: No such file or directory
Is the server running locally and accepting
connections on Unix domain socket "/var/run/postgresql/.s.PGSQL.5432"?
2719 a9f 10/17 15:54:56 ### ValidateConnection() - eRRoR -- Exception in [libpqInterface :: ValidateConnection] Type:[POSTGRE_EXCEPTION] Msg:[PQreset failed to reset the connection]
2719 a9f 10/17 15:54:56 ### libpqInterface() - eRRoR -- Exception in [libpqInterface :: ValidateConnection] Type:[POSTGRE_EXCEPTION] Msg:[PQreset failed to reset the connection]
2719 a9f 10/17 15:54:56 ### ExecutePostgre::init() - eRRoR -- Exception in [libpqInterface :: ValidateConnection] Type:[POSTGRE_EXCEPTION] Msg:[PQreset failed to reset the connection]
2719 a9f 10/17 15:54:56 ### PostgresBrowseAgent::verifyUserInfo() - connection failed
You will find the following errors in the PostGresBackupChild.log file for backup:
9800 d2387700 02/06 14:35:11 259550 PostGresBackupDb::writeFifo() - sh -c "/opt/PostgreSQL/9.0/bin/pg_dump -U postgres -Fc -b --port=5432 'template1' > /opt/install_dir/iDataAgent/jobResults/2/10087/pipe259550_9800" 1
9800 d2387700 02/06 14:35:11 259550 PostGresBackupDb::writeFifo() - System command [sh -c "/opt/PostgreSQL/9.0/bin/pg_dump -U postgres -Fc -b --port=5432 'template1' > /opt/install_dir/iDataAgent/jobResults/2/10087/pipe259550_9800"] failed, ret = 1 out=[] err=[pg_dump: [archiver (db)] connection to database "template1" failed: could not connect to server: No such file or directory
Is the server running locally and accepting
connections on Unix domain socket "/var/run/postgresql/.s.PGSQL.5432"?
]
9800 eddc8740 02/06 14:35:11 259550 PostGresBackupDb::DoBackupDb() - result = failed
9800 eddc8740 02/06 14:35:11 259550 ::PostGresClBackupBase::DoBackupPostGres() - PostGresClBackupBase::DoBackup* returned error
Resolution
In the Instance Properties dialog box, enter the port number in <socket_file_path>:<port> format, and then restart the backup operation.
For example, if socket directory used is /var/run/postgresql,/tmp,/etc/pgsql, and you are using port 5432, enter the port as /var/run/postgresql,/tmp,/etc/pgsql:5432.
PSQL0010: FSBased backup would fail if circular symbolic link is present for a folder or subfolder inside data directory
Symptom
The backup operation goes to pending state. [19:599]: Loss of control process PostGresBackup.exe. The outlined below are the possible causes:
-
The control process has unexpectedly died. Check crash dump or core file.
-
The communication to the control process machine (client1) is disrupted due to network errors.
-
If the machine (client1) is a cluster, it might have failed over.
-
The machine (client1) might have rebooted.
-
The Antivirus/Malware software might be blocking the process.
Cause
The availability of circular symbolic link for a folder or subfolder inside data directory. This causes FS based backup operation to fail.
For example:
/u02/app/postgres/pgdata/as14/data/pg_tblspc/16428 -> /u02/app/postgres/pgdata/as14/data_UC4/data
/u02/app/postgres/pgdata/as14/data_UC4/data/data -> /u02/app/postgres/pgdata/as14/data
Resolution
Remove the circular symbolic link and try to backup again.
PSQL0011: Dump based backup operation fails for PostgreSQL version 8.2 on Windows
Symptom
Dump based backups for PostgreSQL version 8.2 on Windows fail with below error:
PostgreSQL Database: [~Tar Dump format is not supported for PostgreSQL version '8.2'. You need to set registry keys; 'sPGCompDump' , 'sPGStagingDir' to enable Compressed Dump Format. Please refer to the Documentation for more details.~] Data Backup Failed.
Cause
Dump based backup operation is performed using the –Ft option that provides the dump output in Tar format.
Resolution
Create the additional setting sPGCompDump and set its value as Y. This provides the dump in a compressed output format and the dump is staged at the job results folder by default.
You can change the staging location by creating additional setting sPGStagingDir and setting its value as the new staging location.
For instructions on adding the additional setting from the CommCell Console, see Add or Modify an Additional Setting.
PSQL0012: Dump based backup operation fails for table size greater than 8GB
Symptom
PostgreSQL dump based backup for table size greater than 8GB fails with the below error:
PostgreSQL Database: [~Tar Dump format is not supported if table size is more than 8GB. You need to set registry keys; 'sPGCompDump' , 'sPGStagingDir' to enable compressed dump format. Please refer to the Documentation for more details.~] Data Backup Failed.
Cause
Tar format has a limit of 8 GB for backing up individual tables.
Resolution
Create the additional setting sPGCompDump and set its value as Y. This provides the dump in a compressed output format and the dump is staged at the job results folder by default during backups and restores.
You can change the staging location by creating additional setting sPGStagingDir and setting its value as the new staging location.
For instructions on adding the additional setting from the CommCell Console, see Add or Modify an Additional Setting.
PSQL0017: Unable to Associate a PostgreSQL Client to a Storage Policy
Symptom
Unable to associate a PostgreSQL client to a storage policy.
Cause
The log storage policy is set for dump based subclients.
Resolution
-
Download the modify_subclient_template.xml file and save it on the computer from where the command will be executed.
-
To set the log storage policy to the default log storage policy, execute the following command in the CommServe after substituting the parameters values.
qoperation execute –af modify_subclient_template.xml -appName '$[PostgreSQL]' -entity/clientName '$[client_name]' -instanceName '$[INSTANCE_NAME]' –backupsetName '$[DumpBasedBackupSet]' –subclientName '$[subclient_name]' -LogBackupStoragePolicy/storagePolicyName '$[CV_DEFAULT]'
PSQL0018: PostgreSQL log backup fails for Postgres Plus Advanced Server version 9.0
Symptom
PostgreSQL log backup fails for Postgres Plus® Advanced Server version 9.0.
Cause
Postgres Plus® Advanced Server version 9.0 has WAL segment size of 128 GB. But internally it is using 16 MB and log segment files are 16 MB. This is causing incorrect WAL log numbers to be generated, resulting in log backup failure.
Resolution
Create the sWalSegmentSize additional setting as shown in the following table.
For instructions on how to add additional settings from the CommCell Console, see Adding or Modifying Additional Settings from the CommCell Console.
|
Property |
Value |
|---|---|
|
Name |
|
|
Category |
PostGres |
|
Type |
String |
|
Value |
16 MB |
PSQL0020: DumpBased backups on Windows client might fail if there is no space available in Windows temporary directory.
Symptom
Commvault backups, by default, perform pg_dump in windows client using tar format (-Ft).
This doesnot require staging from Commvault side, but Postgresql application uses the system temporary directory as a staging folder for temporary files while generating tar-based dump files (typically C:\temp folder).
If there is no space available in Windows temporary directory, the Dumpbased backups will fail with below error in PostGresBackup.log:
4640 15a8 08/18 00:44:20 115968 PostGresBackupDb::DoBackupDbUsingPipe() - Command [cmd.exe /c ""C:\Program Files\PostgreSQL\10\bin\pg_dump.exe" -U postgres -Ft -b --lock-wait-timeout=60000 --port=5432 "dbname='gk10'" 2> "C:\Program Files\Commvault\ContentStore\iDataAgent\JobResults\CV_JobResults\2\0\115968\CV_Postgres_Error.out""] failed, Error = [pg_dump: [tar archiver] could not write to output file: No space left on device]. Check [C:\Program Files\Commvault\ContentStore\iDataAgent\JobResults\CV_JobResults\2\0\115968\CV_Postgres_Error.out] for detail error
Cause
There was no space available in Windows temporary directory.
Resolution
Allocate a different folder with ample space to accommodate these temporary files by setting an additional setting sPgDumpTempDirectory. Set its value to the full path of the preferred directory.
Or
You have the option to utilize the sPGCompDump additional setting, which generates a database dump in a compressed output format (-Fc). By default, the resulting dump is placed in the job results folder. This specific format requires the staging of the dump output before transferring it to the media agent. If you wish to modify the staging location, you can set an additional setting called sPGStagingDir and assign it to the desired new staging location.
PSQL0021: Permission Denied on Schema During Backup
Symptom
During the PostgreSQL backup operation, the following error messages are displayed:
pg_dump: [archiver (db)] query failed: ERROR: permission denied for schema pushnotification
pg_dump: [archiver (db)] query: LOCK TABLE pushnotification.notification_template IN ACCESS SHARE MODE
Cause
The backup user does not have the required USAGE privilege on the pushnotification schema.
Resolution
Grant the USAGE privilege on the pushnotification schema to the backup user by running the following command:
GRANT USAGE ON SCHEMA pushnotification TO *backup_user*;
PSQL0022: Permission Denied on Table During Backup
Symptom
During the PostgreSQL backup operation, the following error messages are displayed:
pg_dump: [archiver (db)] query failed: ERROR: permission denied for table tenant_sp_product
pg_dump: [archiver (db)] query was: LOCK TABLE quote_config.tenant_sp_product IN ACCESS SHARE MODE
Cause
The backup user does not have the required SELECT privilege on the tenant_sp_product table.
Resolution
Grant the SELECT privilege on the affected table to the backup user by running the following command:
GRANT SELECT ON quote_config.tenant_sp_product TO <backup_user>;
PSQL0023: Backup Fails on Replica Instance Due to Recovery Conflict
Symptom
A PostgreSQL backup operation fails with the following error:
pg_dump: [archiver (db)] query failed: FATAL: terminating connection due to conflict with recovery DETAIL: The user query might have needed to see row versions that must be removed. HINT: In a moment you should be able to reconnect to the database and repeat your command. SSL SYSCALL error: Software caused connection abort (0x00002745/10053)
Cause
The backup is running on a read replica that is in recovery mode. The long-running read queries initiated by pg_dump can conflict with the WAL replay process.
Resolution
Use one of the following options to resolve the issue:
Option 1: Run the Backup on the primary instance.
Run backup operations on the primary PostgreSQL instance to avoid conflicts with recovery.
Option 2: Increase standby delay settings on the replica
Configure the replica to tolerate longer-running queries by increasing the standby delay parameters:
-
max_standby_archive_delay = '30s'
-
max_standby_streaming_delay = '30s'