Deploy Commvault Grid Using Basic Topology with Management Network

HyperScale X nodes can be deployed using a basic topology with a dedicated management network.

In this topology:

  • One interface is configured for CommServe Registration, which is used for data protection traffic and communication with the CommServe server.
  • One interface is configured for the Storage Pool network, which is used exclusively for communication and replication between Commvault Grid nodes.
  • One dedicated 1 GbE interface is configured for the Management network, which is used for management communication, such as accessing DNS services and communicating with the CommServe server.

Use this deployment method when the data protection network is non-routable or isolated, and a separate management interface is required for administrative communication.

Use this procedure to deploy the HyperScale X software using the Hyperscale ISO 3.2312 or higher version.

Note

  • During the setup process, ensure that the following passwords do not contain the special characters ', ", /, ~, or \:

    • Root password
    • Restricted shell user (cvbackupadmin) password
    • CommServe connection password
  • When deployment is complete:

    • Password-based root access is disabled.
    • Firewall protection is enabled.
    • Ransomware protection is enabled automatically.

Before You Begin

  • If you plan to connect to an existing CommServe server, gather the following information before you begin:

    • The fully qualified domain name (FQDN) of the CommServe server.
    • The credentials of an administrative user.
    • Confirmation that TCP ports 8400 and 443 are open between the nodes and the CommServe server.
  • Verify the requirements needed for setting up the Basic Topology With Management Network.

    Tip

    Keep the network names and IP addresses listed in the Network Requirements section of Basic Topology With Management Network handy before you start the configuration. This will help you to accurately add the details during the deployment.

  • The Managed Service Provider (MSP) administrator or the tenant administrator performing the installation must obtain the authorization code.

    For instructions on activating the authorization code, see User Administration and Security.

  • Verify that DNS records have been created and validated for all nodes, as described in DNS Requirements and Validation for Commvault Grid.

  • Verify that the management network is routable and can communicate with the required infrastructure services, including DNS and the CommServe server.

  • Verify that all nodes can communicate with each other on the storage pool network.

Procedure

  1. Log on to one of the nodes using the system console as described in Setting up a Static IP For IPMI. (Do not use PuTTy / SSH to setup the nodes.)

  2. Launch the network configuration interface using the following command:

    # hsxsetup
    

    The Network Configuration page appears.

    embd_Step02 (1)

  3. Configure the data protection interface as follows:

    1. Click Configure interface.

      The Configure interface dialog box appears.

      Basic Deployment With 1 GbE Managment Network (1)

    2. From the Interfaces list, select one of the data protection interfaces. (For example, enpsf3 or enpsf5.)

      Tip

      Hover the cursor over the interfaces to display the speed and MAC address of the physical interface.

    3. Click CREATE.

      The selected interface appears in the Network Configuration page.

      Basic Deployment With 1 GbE Managment Network (2)

    4. From the Network Type list, select CommServe Registration.

      Note

      This network will perform the same role as the data protection network and will also be used to register the node to the CommServe server.

    5. Add the IP Address and Netmask in the respective boxes.

      Once completed your screen should be similar to the one shown in the following image:

      Basic Deployment With 1 GbE Managment Network (10)

  4. Configure the storage pool interface as follows:

    1. Click Configure interface.

      The Configure interface dialog box appears.

      Basic Deployment With 1 GbE Managment Network (1)

    2. From the Interfaces list, select one of the storage pool interfaces. (For example, enpsf4 or enpsf6.)

      Tip

      Hover the cursor over the interfaces to display the speed and MAC address of the physical interface.

    3. Click CREATE.

      The selected interface appears in the Network Configuration page.

    4. From the Network Type list, select Storage Pool. This interface will be used exclusively for communication and replication between the HyperScale nodes.

    5. Add the IP Address and Netmask in the respective boxes.

      Once completed your screen should be similar to the one shown in the following image:

      Basic Deployment With 1 GbE Managment Network (5)

  5. Configure the management interface as follows:

    1. Click Configure interface.

      The Configure interface dialog box appears.

      Basic Deployment With 1 GbE Managment Network (1)

    2. From the Interfaces list, select one of the management interfaces. (For example, enpsf1 or enpsf2.)

      Tip

      Hover the cursor over the interfaces to display the speed and MAC address of the physical interface.

    3. Click CREATE.

      The selected interface appears in the Network Configuration page.

    4. From the Network Type list, select Management. This interface will be used for all management related communication, such as connecting to the CommServe server, accessing the DNS server, etc.

    5. Add the IP Address and Netmask in the respective boxes.

      Once completed your screen should be similar to the one shown in the following image:

      Basic Deployment With 1 GbE Managment Network (6)

  6. Configure the DNS server(s) as follows:

    1. In the Default Gateway box, add the IP address associated with the default gateway.

    2. In the DNS Servers box, add the IP address associated with the DNS Server.

      Click the ADD button to add additional DNS servers. A maximum of 3 DNS servers can be added.

      Note

      Multiple DNS servers are recommended.

      Once completed your screen should be similar to the one shown in the following image: (The number of DNS servers may vary depending on the number of servers available in your environment.)

      Basic Deployment With 1 GbE Managment Network (4)

  7. Click CONFIGURE.

    The software validates the network. (This may take a few minutes to complete.)

    The Network Configuration Summary page appears.

    Basic Deployment With 1 GbE Managment Network (8)

  8. Verify the network configuration and then click CONTINUE.

    Verify the following information.

    • IP address and netmask for the data protection interface accurate.

    • IP address and netmask for the storage pool interface is accurate.

    • IP address and netmask for the management interface is accurate.

    • Hostname and serial number associated with the node is accurate.

      Note

      If you need to change the Hostname do so now. To change the hostname modify and correct the DNS records, (forward and reverse records) as discussed in Setting Up the DNS.

    • Default gateway and DNS servers are accurately configured.

      Note

      If an error is found, or if the hostname was changed, click CHANGE CONFIGURATION to go back and correct the values.

    The Node configuration dialog box appears.

    Tagged vLAN and Bonding (25)

  9. Click one of the following:

    • Click NO, EXIT to configure another node in the storage pool.

      Repeat the steps (steps 1 through 10) from another node.

    • Click YES, CONTINUE if this is the last node in the storage pool.

      The Setup Type page appears.

      Tagged vLAN and Bonding (26)

  10. Click New storage pool setup and then click NEXT.

    The Select Nodes page appears.

    Tagged vLAN and Bonding (27)

  11. Select the nodes as follows:

    1. Click the down arrow Basic (Standalone NIC) (4) at the top right area of the page to view a list of available nodes.

    2. Click and select the nodes that must be included in the storage pool.

      Note

      You can select up to 12 nodes at a time for the initial deployment. Nodes are listed by the respective node names. If one or more nodes are missing from the list, there is likely a cabling or network configuration issue. To troubleshoot, see Troubleshooting Network Configuration Errors.

      If a remote node is not listed, make sure to complete the network configuration on the remote node, and then click ADD and enter the IP address of the node.

    3. Click NEXT.

      The selected nodes will be listed in the Select Nodes page.

      Once completed your screen should be similar to the one shown in the following image: (The number of nodes will vary depending on the number of nodes you select.)

      Tagged vLAN and Bonding (28)

    4. Click NEXT.

      The Network Configuration Summary page appears.

      Basic Deployment With 1 GbE Managment Network (9)

  12. Verify the summary for each node by clicking the tabs associated with each node. Ensure that the nodes are accurately configured and then click NEXT.

    Verify the following information.

    • IP address and netmask for the data protection interface accurate.

    • IP address and netmask for the storage pool interface is accurate.

    • IP address and netmask for the management interface is accurate.

    • Hostname and serial number associated with the node is accurate.

    • All nodes have identical information for the default gateway and DNS servers.

      Note

      If an error is found, click Exit, login to the node in which the error is found and repeat all the steps to correct the error.

    The Storage Pool Details page appears.

    Tagged vLAN and Bonding (32)

  13. Add the following information:

    1. In the Root password and Confirm password boxes, type a secure password for the nodes.

      Tip

      Hover the cursor over the Root password box to view the password requirements.

    2. In the Storage pool name box, type a name for the storage pool associated with the cluster.

      The storage pool name can include numbers and alphabets. Special characters cannot be used in the storage pool name.

      Tip

      Note down the storage pool name. This will be helpful to identify the storage pool in the Command Center.

    3. From the Time zone list, select the time zone in which the nodes are located.

    4. In the Password for Restricted shell user - cvbackupadmin and Confirm cvbckupadmin password boxes, type a secure password for the cvbackupadmin user.

    5. Click NEXT.

      Note

      The setup process configures the network for the nodes. This will take some time to complete.

    The Network Status page appears once the network is configured in the nodes.

    Tagged vLAN and Bonding (33)

  14. Check the status to ensure that all the nodes have a green status to indicate that the network settings is validated and accurate. Click NEXT.

    Note

    If an error is found, hover your cursor over the status icon to view more information on the error. If a node is missing, exit the installer and confirm that all the nodes can ping each other on the storage pool network.

    The Deployment Information page appears

    embd_RA_csinfo (1)

  15. Click Connect to existing CommServe, and then click NEXT.

    The CommServe Credentials page appears.

    Connecting to an Existing CommServe Server (1)

  16. In the CommServe hostname (FQDN) box, enter a fully qualified host name of the existing CommServe server that you are connecting to.

    Note

    TCP Ports 8400 & 443 must be open from the nodes to the CommServe server for the registration to work.

  17. In the Auth-code box, enter the authorization code to connect to the CommServe server.

  18. Click NEXT.

    The software validates the information and will start the installation process. This process may take some time (approximately 45 minutes) to complete. You can monitor the progress using the progress bar.

    Caution

    Do not reboot or stop the installation during this process.

    Once the installation is completed, the Installation page appears.

    embd_SetupCS2 (1)

    If the storage pool creation fails during the installation, you can manually create the storage pool from the Command Center. For more information, see Creating a Commvault Grid Storage Pool.

  19. Click CLOSE.

What to Do Next

Complete the additional configurations that may be required to customize your environment. For more information, see What To Do Next.

×

Loading...